Location
Maine
Methods of suspension between the branch circuit disconnect and the final strain relief. Can mineralac clips (emt stand off clips) be used for this purpose? If not, what are the products that can be used for this purpose.
I appreciate your input....Thanks. 368.56 (B)
 
Oops.... may I clarify

Oops.... may I clarify

Thanks for your links FC.

What can be used in between the disconnect and the "take up support device"?
"approved means" for 368.56 (B)(1)?
Providing the exception to 368.56 (BA)(2) applies and we support the wire every 2.5 meters/8 feet.

Did I miss something on the Kellems link?

Thanks again.
 
I don't know what straps are listed for the cable you are using.
I would ask your supply house what straps
are listed for that cable.
Maybe someone else on this forum can help you out with an approved strap.
 