Good morning. I can't seem to find an answer in the code. Does a hardwired garbage disposal require GFCI protection.
Not that I can find either. I say not required.Good morning. I can't seem to find an answer in the code. Does a hardwired garbage disposal require GFCI protection.
I don't think a garbage disposal is going to wash your dishes very well, so that's not going to be applicable. : - )(7) Dishwashers
Yeah, I read that wrong. Thanks.I don't think a garbage disposal is going to wash your dishes very well, so that's not going to be applicable. : - )
Cheers, Wayne
NopeGood morning. I can't seem to find an answer in the code. Does a hardwired garbage disposal require GFCI protection.
If you put that in my house, I’d make you remove it.What state are you in? Some states have additional requirements, my state Oregon has 26 pages of exceptions and additions to nfpa 70. Called table 1E, although not required I use dead face GFCI’s and sell as a unique safety upgrade right next to the switch.
You would be amazed how many people want them but I am in a loony liberal area, I only have them where required and my state only requires 15& 20 amp 120v to have them (other than a hot tub) 240v within 6’ from a sink for my deep fryer and no GFCI not required in OR. Table 1E exemption.If you put that in my house, I’d make you remove it.
Thats nice you at least offer the choice, with all the other insurance people wast money on out there these days like home warranty insurance, trip insurance on your trip insurance, or health insurance for your health insurance, and then getting insurance to actually cover anything when you need it, combined with the decline in quality of household appliances if figure an few extra $ on non required GFCI breakers to be good insurance for those the opt for it.You would be amazed how many people want them
422.5 Ground-Fault Circuit-Interrupter (GFCI) Protection
for Personnel.
(A) General. Appliances identified in 422.5(A)(1) through
(A)(7) rated 150 volts or less to ground and 60 amperes or less,
single- or 3-phase, shall be provided with Class A GFCI protection
for personnel. Multiple Class A GFCI protective devices
shall be permitted but shall not be required.
(1) Automotive vacuum machines
(2) Drinking water coolers and bottle fill stations
(3) Cord-and-plug-connected high-pressure spray washing
machines
(4) Tire inflation machines
(5) Vending machines
(6) Sump pumps
(7) Dishwashers
Informational Note: Section 210.8 specifies requirements
for GFCI protection for the branch-circuit outlet
where the covered location warrants such protection.
But like others mentioned this would require AFCI according to: NEC 2023: 210.12(B)(1) Kitchens, or NEC 2017: 210.12(A)Thats nice you at least offer the choice, with all the other insurance people waste money on out there these days like home warranty insurance, trip insurance on your trip insurance, or health insurance for your health insurance, and then getting insurance to actually cover anything when you need it, combined with the decline in quality of household appliances if figure an few extra $ on non required GFCI breakers to be good insurance for those the opt for it.
Especially considering the time and current it takes to trip a regular 20A 120V breaker, I'd rather not have my disposal dumping 25 amps down the EGC for a few hours till the breaker decides to trip, if it ever does.
And I have never seen a disposer (or dishwasher) that was not hard-wired.Not sure I've seen a disposal that is hardwired, most have been corded, but I guess they are out there.