Harmonic Currents?

Status
Not open for further replies.

The Iceman

Senior Member
Location
Florida
Can anyone help me better understand Harmonic Currents. For example, an office building with personal computers, fluorescent lighting, and copiers supplied by a three-phase wye service. I understand that these are nonlinear loads, that produce higher frequencies, and results in larger currents on the grounded neutral conductor. This is my basic understanding of Harmonic Currents. Can anyone elaborate on this subject?
 

The Iceman

Senior Member
Location
Florida
Alot of people believe that Harmonics caused by nonliear loads will trip GFCI protected circuits, such as fluorescent lights. Sorry about asking another question, but is this true?
 

iwire

Moderator
Staff member
Location
Massachusetts
Even with harmonic currents the current 'out' on the circuit will equal the current 'in' on the circuit.


I think florescent fixtures can trip GFCI protected circuits by current leakage of the secondary side of the ballast and lamps.
 

Besoeker

Senior Member
Location
UK
Can anyone help me better understand Harmonic Currents. For example, an office building with personal computers, fluorescent lighting, and copiers supplied by a three-phase wye service. I understand that these are nonlinear loads, that produce higher frequencies, and results in larger currents on the grounded neutral conductor. This is my basic understanding of Harmonic Currents. Can anyone elaborate on this subject?
Many single phase loads take non-linear currents resulting in harmonics. In particular, 3rd and multiples of it (triple-n) are particularly troublesome for the rating of neutrals. This because the third and its multiples are in phase from all three phases of the input supply and add together in the neutral rather than cancelling.
It's maybe easier to see if you draw it out.
 