electricalperson
Senior Member
- Location
- massachusetts
today i opened a 3 phase 120v/208v panel and taken current measurments. phase A was around 7 amps B and C were 10 amps and about 8 amps. the neutral was 10.8 amps. the panel fed computers and other nonlinear loads. i believe the current i measured was mostly harmonic currents instead of 3 or 4 amps of unbalanced current. in a book i read it says the 3rd harmonic can double the neutral current. it shown a diagram of each phase with 20 amps and a 40 amp load on the neutral.
was that book showing the worst case scenario with harmonics and what i measured more what reality is like?
was that book showing the worst case scenario with harmonics and what i measured more what reality is like?