EmagSamurai
Member
- Location
- Alabama
I have a simple question that I've been struggling to come up with a simple answer for. I was presented with the following statement today:
"Any motor larger than 5 hp, driven by a VFD, should be delta wound"
The explanation for this was that the harmonics resulting from the VFD will not have a neutral to flow down on a WYE wound motor, so the imbalance currents will be carried by the other phases. A WYE wound motor will see imbalance current 1.73 times higher than a delta motor, which will result in reduced life expectancy. DELTA wound motors typically have larger conductor windings, so they can handle the added heat.
I've never heard this before, and I can't even remember a time where a neutral was brought out of a motor regardless of the size.
Is this a rule of VFDs that I just haven't been let in on?
The system in question is ungrounded delta/delta (4160/480) supplying the VFDs, which feed a 7.5 hp YY/Y motor.
"Any motor larger than 5 hp, driven by a VFD, should be delta wound"
The explanation for this was that the harmonics resulting from the VFD will not have a neutral to flow down on a WYE wound motor, so the imbalance currents will be carried by the other phases. A WYE wound motor will see imbalance current 1.73 times higher than a delta motor, which will result in reduced life expectancy. DELTA wound motors typically have larger conductor windings, so they can handle the added heat.
I've never heard this before, and I can't even remember a time where a neutral was brought out of a motor regardless of the size.
Is this a rule of VFDs that I just haven't been let in on?
The system in question is ungrounded delta/delta (4160/480) supplying the VFDs, which feed a 7.5 hp YY/Y motor.