There is some place here that their ballast (T8 120V electronic) keep failing (several on each circuit per month).
Here what I have :
Phase A: 82A
Phase B: 94A
Phase C: 81A
Neutral: 19A
THD%f
Phase A: 9
Phase B: 6.9
Phase C: 7
Neutral: 485
All the neutral harmonics are coming from the 3rd one in the neutral cable (473.4).
I know that electronic ballast have harmonics between 18 to 32%. So the harmonics in the phase A,B,C seems quite normal, but the neutral one is alot? can that be the cause of the ballast failling?