hde_electric
If harmonics are such a big problem on a 3 phase system why use it then on new office buildins with a lot of non-linear loads and use 120/240 system instead? Will somebody explain please. Thank you.
For the whole article go here:<big snip>Harmonics only mean trouble if the power system is not designed to handle them. High harmonic neutral currents are a problem only if the neutral is not properly sized. Current harmonics are not a problem to a transformer if it is derated appropriately. Even some voltage distortion below 8% THD at the point of utilization) is acceptable as long as sensitive equipment is not affected. However, it is always important to be aware of the presence of harmonics and to try to minimize them by purchasing low distortion electronic ballasts and reactors for PWM ASDs. This will not only keep the harmonics in check and improve the power factor in the facility, but will also save energy by reducing losses on power system components. In addition, any time there is a considerable increase of non-linear loads, it is important to check power system components to prevent problems.
<snip>
CapacityOriginally posted by hde_electric:
But why are 120/240 systems not used in some offices?
I can think of two reasons. First, let?s presume a total load of 100 KVA. If you serve it with 120/240, the current will be 416 amps, and you will need a 600 MCM feed (or smaller parallel conductors). If you serve it with 120/208, the current will be 120 amps, and you will only need an AWG #1. Secondly, a large single phase load would cause a balance problem for the utility system. They might be able to achieve an overall balance by feeding other nearby customers with the other single phases, but that?s not the ideal solution. Better to have each customer balance their loads by using a 3-phase service.Originally posted by hde_electric: But why are 120/240 systems not used in some offices?
For more on Transformer Ratings go here:"K" Factor Transformer Rating:
<big snip>In the 1980's, power quality engineers began encountering a new phenomenon: non-linear loads, such as computers and peripherals, began to exceed linear loads on some distribution panels. This resulted in large harmonic currents being drawn, causing excessive transformer heating due to eddy-current losses, skin effect, and core flux density increases.
Standard transformers, not designed for nonlinear harmonic currents were overheating and failing even though RMS currents were well within transformer ratings.
In response to this problem, IEEE C57.110-1986 developed a method of quantifying harmonic currents. A "k" factor was the result, calculated from the individual harmonic components and the effective heating such a harmonic would cause in a transformer. Transformer manufacturers began designing transformers that could supply harmonic currents, rated with a "k" factor. Typical "K" factor applications include:
K-4: Electric discharge lighting, UPS with input filtering, Programmable logic controllers and solid state controls
K-13: Telecommunications equipment, UPS systems, multi-wire receptacle circuits in schools, health-care, and production areas
K-20: Main-frame computer loads, solid state motor drives, critical care areas of hospitals
"K" factor is a good way to assure that transformers will not overheat and fail. However, "K" factor is primarily concerned with thermal issues. Selection of a "K" factor transformer may result in power quality improvement, but this depends upon manufacturer and design. <big snip>
absolutely.Does anyone else ever wonder why almost all of the information on this "problem" comes from organizations that have an economic interest in selling products to fix the "problem"???
I'm not sure if it is worth arguing your point with my anecdotal situations, but I have found tremendous information regarding this possible problem from the IEEE, trade magazines and questions/discussions with on site technicians.Does anyone else ever wonder why almost all of the information on this "problem" comes from organizations that have an economic interest in selling products to fix the "problem"???