Hi all,
Harmonic interference from fluorescent lights is a subject that I don't know much about but its time I learned. Here is my problem:
I have a nursing home customer that has some patients that are not permitted to go outside by themselves. The exit door is equipped with an alarm system that sounds when a restricted patient approaches the exit and is within 4 or 5 feet of the door. There is a device that care givers attach to them that sets off the alarm. This allows anyone else to enter or exit without setting off the alarm. This alarm system was working fine for years until we retrofitted the existing T12 ceiling fixtures with T 8 ballasts and lamps. The alarm system now allows the restricted patients to get within one foot of the door before alarming which reduces the response time for any caregivers to intercept the restricted patient. The alarm system is adjustable but one foot is the best we could do.
Here is the real puzzler: Since the alarm system is fed from a generator back up panel, we shut off the breaker that fed about one of every four ceiling lights from the same panel. The exit door alarm system operated the way it did before the retrofit. It was perfect. None of the other ceiling lights that were not on generator back up and were still turned on had any effect on the exit doors alarm system. I determined that the gen back up ceiling lights and alarm system were being fed from the same phase so I moved the lights to a different phase. No difference. So we tried replacing the ballasts in the gen back up fixtures with high efficiency ballasts. It actually made the problem worse.
The maintenance director is anxious to get things back to normal. So I am thinking about installing the low voltage wire for the door alarm system in EMT since it now travels through the ceiling without any protection. I welcome any thoughts on this matter. Thanks in advance.
Harmonic interference from fluorescent lights is a subject that I don't know much about but its time I learned. Here is my problem:
I have a nursing home customer that has some patients that are not permitted to go outside by themselves. The exit door is equipped with an alarm system that sounds when a restricted patient approaches the exit and is within 4 or 5 feet of the door. There is a device that care givers attach to them that sets off the alarm. This allows anyone else to enter or exit without setting off the alarm. This alarm system was working fine for years until we retrofitted the existing T12 ceiling fixtures with T 8 ballasts and lamps. The alarm system now allows the restricted patients to get within one foot of the door before alarming which reduces the response time for any caregivers to intercept the restricted patient. The alarm system is adjustable but one foot is the best we could do.
Here is the real puzzler: Since the alarm system is fed from a generator back up panel, we shut off the breaker that fed about one of every four ceiling lights from the same panel. The exit door alarm system operated the way it did before the retrofit. It was perfect. None of the other ceiling lights that were not on generator back up and were still turned on had any effect on the exit doors alarm system. I determined that the gen back up ceiling lights and alarm system were being fed from the same phase so I moved the lights to a different phase. No difference. So we tried replacing the ballasts in the gen back up fixtures with high efficiency ballasts. It actually made the problem worse.
The maintenance director is anxious to get things back to normal. So I am thinking about installing the low voltage wire for the door alarm system in EMT since it now travels through the ceiling without any protection. I welcome any thoughts on this matter. Thanks in advance.