Re: Harmonics
Cl/amp meters show neutral-triplen harmonics in greater magnitudes than distorted volts do.
My 1996 ShureTest (Quick Start) guide states, "..3d harmonic computer loads will drop the peak voltage faster than the RMS voltage. This measurement is a quick guage of the harmonic distorion effects of a computer load. Heavy 3d harmonic loads cause the voltage sine wave to flat-top, affecting the ride-through capability of less expensive switch mode power supplies, increasing the chance of a reboot or lockup during a low voltage event..."
Unfortunately, while indicating 3rd order voltage harmonics less than 0.7% and THD voltage below 3.0% my ShureTest Peak-voltage function always shows ~7.0vac lower than its (RMS * 1.414) verified with my DMM. So, my ShureTest ST-1THD either drifts Peak-volt calibration, or this miniscule 3rd harmonic flat tops voltage peaks, from all service distributions in my region.
A scope or graphic-wave analyzer would best show flat-top or distorted wave forms, and solve my ShureTest calibration mystery, but no such animal exists without investing a fortune in the Los Angeles area. The work I get would not justify the cost of calibrating some of these power quality analyzers. But, I could really use one to verify these cheezy ShureTest values and the CMV proficiencies.
I found some of this information in my ShureTest ST-1THD manuals, which indicate when circuits arn't near overload, nor contain an unbalanced load between three phases, a common mode voltage G-N > 2.0 RMS likely indicates harmonic currents.
The caveat is that CMV varies widely with shared neutrals, changes in line noise, loads, and panel proximity. Further, with no such animals above in my aging residence their exists one duplex @ 2.2 vac G-N, with no load, which is likely from a hacked-in EGC, landed on warm rather than cold water pipes.
So, RMS cl/amp meters, THD analyzers, and scopes seem more dependable than CMV's > 2vac as a harmonic indicator. CMV may show relative differences in neutral harmonics at several places in a distribution system. If its not following panel proximity or shared neutrals, perhaps CMV could point to neutral THD increases with proximity to noisy equipment. But, that effort is fruitless where limits on device THD are specified according to phase conductor and require sampling with cl/amp meters anyway.
Except for ShureTest claims, I could'nt find any test evidence of using CMV as a harmonic indicator anywhere. Someone needs to compare this thing along side a real scope, and check this calibration-drift issue.