I have a project where the facility has several 4160 to 480V substations. Down stream of each of these are a multitude of existing 6 pulse drives.
As part of our project we adding drives. Obviously we need to conduct a harmonic study which is inclusive of the old and the new to know whether or not be need filters, active filters, etc. But the question came up:
Will the harmonics on one of the multiple system. i.e. off of one of the 4160V substations effect the other 480V systems which are via a separate substation.
All of the 4160V to 480V transformers are delta wye. Given that this is the case, I believe the answer is NO. We need to look at each separate 480V system relative to the impedance of the transforer(s) feeding into that system but that is all.
Sanity check here. Do you agree?