I just completed a power quality test on building with power coming to 480 volt service panel showing 99.8% THD has the max and 35% THD min. Has anyone ever come across THD results that high?
I just completed a power quality test on building with power coming to 480 volt service panel showing 99.8% THD has the max and 35% THD min. Has anyone ever come across THD results that high?
I agree, talking about THD as a percent is misleading. Get a number for harmonic current or harmonic voltage. A 20A circuit with 1A of load, all high harmonics, is not a problem. A 20A circuit with 16A of load and 1A of harmonics, is probably not a problem. A 20A circuit with 16A of harmonic current is a problem.
.
Assuming you mean TDH for current, then a figure of 35% wouldn't surprise me. Today I completed an analysis of a piece of kit that had about 48% of just 5th harmonic. Even visually, it is a very distorted waveform.I just completed a power quality test on building with power coming to 480 volt service panel showing 99.8% THD has the max and 35% THD min. Has anyone ever come across THD results that high?
I just completed a power quality test on building with power coming to 480 volt service panel showing 99.8% THD has the max and 35% THD min. Has anyone ever come across THD results that high?
Understand, when one has the test equipment and is unsure NOTHING beats doing what you did. I have learned a lot doing the old hands on and then trying to determine what is this?