Have to hang Quads from ceiling in Commercial Building

Status
Not open for further replies.

bjp_ne_elec

Senior Member
Location
Southern NH
I have a commercial facility that wants Quads dropped from the ceiling - actually it's a dropped acoustical ceiling, so I'll have to be anchoring to either a steel ceiling joist or the wall in some cases. They build electronic equipment and tend to move things around on wheels. Most of the things they need to plug in are roll around racks with cards mounted on them. They generally only require a 120 V outlet - and they want the quad to have two circuits - one per duplex.

Does anyone have any photos of what you've worked out for a solution? I was thinking some type of spring thingy that would be used to just support the SO card from above - and just take the shock off if someone snagged the drop.
 

masterinbama

Senior Member
I used to do a lot of work for a local electronics manufacturer. We would just drop 12-3 cord with kellum grips on each end supporting a FS box for GP outlets and twist-loks for dedicated circuits. We would hang them 7' AFF so people would not bump their heads on them. A new room with no equipment in it reminded me of that movie Coma
 

blueheels2

Senior Member
Location
Raleigh, NC
Occupation
Electrical contractor
I used some of the Starline busway in a lab at Sprint about a year ago. They had a bunch of server racks that they were constantly moving around. They were nice looking and easy to install.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I have a commercial facility that wants Quads dropped from the ceiling - actually it's a dropped acoustical ceiling, so I'll have to be anchoring to either a steel ceiling joist or the wall in some cases.

Make sure you don't run the flexible cord above or through the suspended ceiling. (See 400.8(2) & (5))

I also agree, use the Woodhead boxes, they are specifically designed for cord drops and hold up very well.

Chris
 

bjp_ne_elec

Senior Member
Location
Southern NH
Make sure you don't run the flexible cord above or through the suspended ceiling. (See 400.8(2) & (5))

I also agree, use the Woodhead boxes, they are specifically designed for cord drops and hold up very well.

Chris
Chris - funny you should mention that - the present drops installed all have the SO cord going up in to the ceiling. I'll have to come up with some method of installing a box just below the ceiling. All the drops are about a foot off the wall - so I'd like to be at least consistent with that. Have to explain to the Plant Manager that I can use the same method of install. I'll have to explain that to him, as he seems to want to keep every thing consistent.
 

bjp_ne_elec

Senior Member
Location
Southern NH
Chris - funny you should mention that - the present drops installed all have the SO cord going up in to the ceiling. I'll have to come up with some method of installing a box just below the ceiling. All the drops are about a foot off the wall - so I'd like to be at least consistent with that. Have to explain to the Plant Manager that I can use the same method of install. I'll have to explain that to him, as he seems to want to keep every thing consistent.

I should have said that I can't use the same method - as the present method on the older installs is to bring the SO cord up in to the ceiling to a JB.
 

iwire

Moderator
Staff member
Location
Massachusetts
Keep in mind what the others have said about the box at the bottom of the pendent.

Using a box with KOs is definitely a violation, a standard 'bell box' has threaded hubs but is still not designed / listed to be supported from the threaded hubs. If you don't use the Woodhead pendent boxes I suggest a malleable steel FS box with threaded hubs.
 

bjp_ne_elec

Senior Member
Location
Southern NH
One issue - I couldn't find the Woodhead boxes - I just found the Reel and the Kellum grips. My dilemma is how to mount the box cleanly below the ceiling. All the other existing installs have a 4" square JB above the ceiling with SO cord coming out - with Kellum grip attached to the block wall. If I understand the code correctly, I can no longer allow the SO cord to drop from above the ceiling to below. It's a standard grid ceiling, but I don't want to support a box from it.

Any solutions with pics would be great!

Thanks
 

barclayd

Senior Member
Location
Colorado
Using a box with KOs is definitely a violation,

Is that somewhere in 314?
I've seen 4 sq's and Bell boxes both used for cord drops. I don't remember ever seeing an FS/FD box, though - those would really HURT if you get them swinging.

thanks
db
 

electricalperson

Senior Member
Location
massachusetts
Is that somewhere in 314?
I've seen 4 sq's and Bell boxes both used for cord drops. I don't remember ever seeing an FS/FD box, though - those would really HURT if you get them swinging.

thanks
db

all the 4 inch squares i see used as pendant drops are dangling by the cord because the lock nut fallen off. thats why its a violation. constant twisting and bending will make that locknut loosen and come off and then you have exposed conductors that will probably short out. those conductors are supporting the box by the terminal screws on the device
 

bjp_ne_elec

Senior Member
Location
Southern NH
I like the ideas on the receptacle end, but was looking more for some ideas on how to cleanly get something mounted where I could transition the SO cord out of. Actually, the SO cord going in to the sealing is "neat" as you only need a small hole in the acoustical tile - but now the code doesn't allow that. One solution is a box on the wall just below the ceiling, but I got to figure, one of you guys has something more "clever" than that.

Thanks
 

iwire

Moderator
Staff member
Location
Massachusetts
I would support a 4" octagon box in the ceiling with a Caddy 512 bar

512HD.jpg


Put a 4" round WP cover on that box

17042.S213WHE_4.jpg


Screw a cable grip into that.

Hubbell-07401023-rw-85598-150868.jpg
 

iwire

Moderator
Staff member
Location
Massachusetts
I have done it like that but I can not take credit for it.

I usually Tek Screw the 512 bars to the grid and run a ceiling tie wire from the building to the hook on the 512 bar.
 

barclayd

Senior Member
Location
Colorado
all the 4 inch squares i see used as pendant drops are dangling by the cord because the lock nut fallen off. thats why its a violation. constant twisting and bending will make that locknut loosen and come off and then you have exposed conductors that will probably short out. those conductors are supporting the box by the terminal screws on the device

But is it a violation of 314 something? We've used female Kellems grips with chase nipples and they've never come loose.
thanks
db
 