zemingduan
Senior Member
- Location
- Philadelphia,PA
- Occupation
- Electrical Designer
I am working on an electrical design of a building that is an old 120/240V 2ph 5 wire electrical system in Philadelphia. The new elevator is 208V 3ph. And this building is required to have stand by power for the elevator since it's over 6th floor but not high rise. I design a standby power panel which supplies the elevator motor, car lighting, hoist way GFCI outlets, machinery space outlets and pit sump pump.
I have seen a 120/240V 2PH 5Wire to 208V 3ph 3wire before. I want to see if there is a 120/240V 2PH 5Wire to 120Y/208V 3ph 4wire transformer. So that I can supply the normal power of the standby power panel from the transformer secondary. Thus I can avoid another 208V 3ph delta to 120/208V 3ph 4wire whey transformer.
By the way, are the car lighting and hoist way and machinery space outlets required to hooked to the generator? I search the IBC. It looks like they are required only for high rise building fire service or self evacuation elevators.
I have seen a 120/240V 2PH 5Wire to 208V 3ph 3wire before. I want to see if there is a 120/240V 2PH 5Wire to 120Y/208V 3ph 4wire transformer. So that I can supply the normal power of the standby power panel from the transformer secondary. Thus I can avoid another 208V 3ph delta to 120/208V 3ph 4wire whey transformer.
By the way, are the car lighting and hoist way and machinery space outlets required to hooked to the generator? I search the IBC. It looks like they are required only for high rise building fire service or self evacuation elevators.