Someone please quickly help me out I understand article 230 States service conductors need to be sized per the load connected
But that being said take this scenario into play 3 family building total of four meters
Customer wants as follows 200-amp for his apartment
100 in each other apartment
so a total of 3 one hundred amp panels and 1 200 amp panel
Coming off the utility do I basically add up the sum of all breakers to size the service entrance conductors basically needing a conductor size to be able to handle a 500 amp load
There is no engineering a load calculations this is strictly based on providing the customer they are asking for