I read article 670. It seems like none of the nameplates on the machines I need to size wire and breakers for include the information required by 670.3(a). I need to price material for about 20 machines because a shop owner is combining two shops into one at a new location. That is one big problem.
In another shop the nameplate on Tsugami BO326-II says 64 amps. I guess this means FLC of all motors inside that will run at once? The machinist ran it on a 50 amp breaker for three years and never had a problem but now that he is running higher rpm jobs the breaker tripped. Tsugami sent me a installation sheet that said it requires a 95 amp service if combined with the chiller pump and V2 MP pump which is being used. There is a bar feeder wired to it too. The machine has a 100amp breaker on it.
So, to size the wire correctly I guess I can look at specs to find highest rated motor, x it by 1.25, add that to the rest of the flc on machine name plate plus flc of pumps and bar feeder?
If I did this and ran #3 or #2 copper to it can I size the breaker to 100 (because that's the size breaker on machine) + 1.25 x highest motor plus other flcs? That sounds super huge.
It seems like no one can tell me a concrete method of providing power these things and everyone just runs #6 and puts them on 50 or 60 amp breakers.
Also, do all these things come with a breaker inside and is it considered a means of disconnect?
If anyone can suggest a book covering this or a way to learn this stuff I would totally appreciate it. Thanks in advance for anyone taking the time to read this.
In another shop the nameplate on Tsugami BO326-II says 64 amps. I guess this means FLC of all motors inside that will run at once? The machinist ran it on a 50 amp breaker for three years and never had a problem but now that he is running higher rpm jobs the breaker tripped. Tsugami sent me a installation sheet that said it requires a 95 amp service if combined with the chiller pump and V2 MP pump which is being used. There is a bar feeder wired to it too. The machine has a 100amp breaker on it.
So, to size the wire correctly I guess I can look at specs to find highest rated motor, x it by 1.25, add that to the rest of the flc on machine name plate plus flc of pumps and bar feeder?
If I did this and ran #3 or #2 copper to it can I size the breaker to 100 (because that's the size breaker on machine) + 1.25 x highest motor plus other flcs? That sounds super huge.
It seems like no one can tell me a concrete method of providing power these things and everyone just runs #6 and puts them on 50 or 60 amp breakers.
Also, do all these things come with a breaker inside and is it considered a means of disconnect?
If anyone can suggest a book covering this or a way to learn this stuff I would totally appreciate it. Thanks in advance for anyone taking the time to read this.