Has anybody heard of the term ‘Hawaiian tie in’?
We are a solar company in California. We have been told that 'Hawaiian tie in' is common practice out east.
With a Hawaiian tie in, we remove all load breakers and put a lug kit to feed a sub where we relocate all house loads.
This makes the MSP a ‘supply side’ panel. Even if we leave a main disconnect breaker inside. (Warning plaque - no load breakers allowed)
And because of that (if the situation is needed), we can leave the solar breaker(s) in there. (and they will be a supply side connection – not 120% rule)
All of that does make sense to me. (I just hope we can get the AHJ’s and inspectors on board!)
Would any of you happen to have any code references on this?
Would be much appreciated, Thanks!