1.) National Electrical Code section 210.4
2.) New Text
3.) Proposal:
Haywire Circuits: Loads shall not be supplied by tapping one or more conductors of a branch circuit and 1 or more conductors of another branch circuit. 15-ampere to 50-ampere single-phase branch circuits shall be wired so that GFCI protection for people or equipment can be applied at or near the supply panelboard.
A nonmetallic sheathed cable type NM, NMC, or UF that is installed as a retrofit with nonmetallic boxes to correct haywiring shall be permitted to take any convenient route.
In new installations where 2 or 3 nonmetallic sheathed cables types NM, NMC, SE, or UF are installed in accordance with 300.3(B)(3) to provide 4 to 9 current carrying conductors between 2 boxes shall be installed within 4 inches ( 100 millimeters ) of each other and shall pass entirely on 1 side of any metal object such as plumbing or ductwork.
4.) Justification and Reasoning:
Some electricians are still wiring stairway lights by tapping a hot wire on the lower floor, going through the 3-ways and 4-ways with 2-wire with ground type NM cable, and then tapping a neutral that is on a different circuit on the upper floor. This creates unexpected shared neutral circuits that can be harzardous to service and the shared neutral could be overloaded if both overcurrent devices are somehow on the same phase. Haywire circuits also make installation of ground fault circuit interrupters and arc fault circuit interrupters for the whole branch circuit or a large part of it impossible without having to do major extra work.
There is no excuse for NOT doing light switches by the book. Haywiring was done back in the days of knob and tube wiring where a #6 common neutral wire ran the length of a floor and is an obsolete concept.
When 2 or 3 cables are installed to serve the logical equivalent of a single cables then the workmanship needs to be done similar to a single cable.
[ April 17, 2005, 02:28 AM: Message edited by: mc5w ]
2.) New Text
3.) Proposal:
Haywire Circuits: Loads shall not be supplied by tapping one or more conductors of a branch circuit and 1 or more conductors of another branch circuit. 15-ampere to 50-ampere single-phase branch circuits shall be wired so that GFCI protection for people or equipment can be applied at or near the supply panelboard.
A nonmetallic sheathed cable type NM, NMC, or UF that is installed as a retrofit with nonmetallic boxes to correct haywiring shall be permitted to take any convenient route.
In new installations where 2 or 3 nonmetallic sheathed cables types NM, NMC, SE, or UF are installed in accordance with 300.3(B)(3) to provide 4 to 9 current carrying conductors between 2 boxes shall be installed within 4 inches ( 100 millimeters ) of each other and shall pass entirely on 1 side of any metal object such as plumbing or ductwork.
4.) Justification and Reasoning:
Some electricians are still wiring stairway lights by tapping a hot wire on the lower floor, going through the 3-ways and 4-ways with 2-wire with ground type NM cable, and then tapping a neutral that is on a different circuit on the upper floor. This creates unexpected shared neutral circuits that can be harzardous to service and the shared neutral could be overloaded if both overcurrent devices are somehow on the same phase. Haywire circuits also make installation of ground fault circuit interrupters and arc fault circuit interrupters for the whole branch circuit or a large part of it impossible without having to do major extra work.
There is no excuse for NOT doing light switches by the book. Haywiring was done back in the days of knob and tube wiring where a #6 common neutral wire ran the length of a floor and is an obsolete concept.
When 2 or 3 cables are installed to serve the logical equivalent of a single cables then the workmanship needs to be done similar to a single cable.
[ April 17, 2005, 02:28 AM: Message edited by: mc5w ]