I have a solenoid valve in a Class 1 Div 1 area. The solenoid is rated for the area. Is a sealoff reqired on a solenoid. There are no limits switches. Thanks
Joe McKenna said:I have a solenoid valve in a Class 1 Div 1 area. The solenoid is rated for the area. Is a sealoff reqired on a solenoid. There are no limits switches. Thanks
It may seem counter intuitive, since an enclosure that is required to be explosionproof in Division 2 is also required to be sealed; but a properly rated solenoid in Division 1 would not need a seal unless the conduit opening were 2? or larger. See 501.15 (A)(1)(1) and (2) and the subsequent text and Exceptions.Joe McKenna said:I have a solenoid valve in a Class 1 Div 1 area. The solenoid is rated for the area. Is a sealoff reqired on a solenoid. There are no limits switches. Thanks
For the purposes of this section, high temperatures shall be considered to be any temperatures exceeding 80 percent of the autoignition temperature in degrees Celsius of the gas or vapor involved.
rbalex said:It may seem counter intuitive, since an enclosure that is required to be explosionproof in Division 2 is also required to be sealed; but a properly rated solenoid in Division 1 would not need a seal unless the conduit opening were 2? or larger. See 501.15 (A)(1)(1) and (2) and the subsequent text and Exceptions.
A solenoid with a proper ?T-rating? is not considered to be a device ??that may produce arcs, sparks, or high temperatures that are considered to be an ignition source in normal operation.?
A proper ?T-rating? would not permit a high temperature. Extracted from 501.15(A)(1):
It is very straightforward. I have cited the appropriate Code Sections [501.15 (A)(1)(1) and (2) and the subsequent text and Exceptions.]weressl said:Unfortunately I do not think is that straightforward.
What is your basis for this statement?weressl said:Your stipulation would be true IF the manufacturer specifically spelled out that external seal is not required.
This is simply an assertion on you part. Again, what is the basis for this statement?weressl said:Division 1 testing involves in testing the EXTERNAL temperatures developed for the device, not the internal maximum temperatures. Since Division 1 mode presumes internal failure and there is no internal thermal protection for the coil, it is possible that the coil can overheat.
Where did you get this idea?weressl said:If the solenoid has no explosionproof enclosure, it would indicate that the internal temperatures HAVE been considered and no explosion containment is needed. You still have to install a seal to maintain the explosion containment not of the solenoid, but of the conduit system.
rbalex said:It is very straightforward. I have cited the appropriate Code Sections [501.15 (A)(1)(1) and (2) and the subsequent text and Exceptions.]
What is your basis for this statement?
This is simply an assertion on you part. Again, what is the basis for this statement?
Where did you get this idea?
I?m sorry I offended you.weressl said:The basis of my statement was explained in the paragraph(s) following the assertion.
My assertion is based on the UL testing process for ther approval. There are different testing proecss for each type of equipment and type of construction. The UL testing for Division 1 and Division 2 luminaires, for example, involves the placing of 30-40 RTD's on the external surface of the luminare for Division 1 test and both externally and internally in the case of Division 2 tests. The luminaires built for Division 1 are expected to withstand an internal explosion, eg. it is expected that a failure will produce a source of ignition inside and in that case it is not material to establish and verify a T-rating for the internals of the unit. In the case of Division 2 luminares no internal explosion is permitted so the hottest point must be found both internally and externally for the T-rating.
Your last question concerned a paragraph with several statements and since you weren't specific as to what part do you question, I can not answer it.
It would be helpful if you engage in a dialog, instead of sniping. Thinking does not hurt. Try it sometimes.
Joe McKenna said:I have a solenoid valve in a Class 1 Div 1 area. The solenoid is rated for the area. Is a sealoff reqired on a solenoid. There are no limits switches. Thanks
justdavemamm said:Here's my take from what I have seen installed:
1. If the SV is I.S. so you have an I.S. barrier/isolator feeding it, then No.
2. If the SV is XP rated and does not have it's own built in seal, then Yes.
3. If the SV is XP rated and has a built in seal (as documented by the mfg), then No.
justdavemamm said:Here's my take from what I have seen installed:
What you have seen should not the basis of your analysis; what the NEC says should be. Read Section 501.15 (A)(1) carefully.justdavemamm said:1. If the SV is I.S. so you have an I.S. barrier/isolator feeding it, then No.
2. If the SV is XP rated and does not have it's own built in seal, then Yes.
3. If the SV is XP rated and has a built in seal (as documented by the mfg), then No.