timm333
Senior Member
- Location
- Minneapolis, MN
- Occupation
- Electrical Design Engineer
I am trying to figure out the hazardous area classification of outdoor storage tank. It looks that the area within 10-feet of the tank is Class 1 Division 2. After 10-feet the area is still Class 1 Division 2, but it is only up to a height of 3-feet from the floor. The classified area continues until it touches the dike; after the dike the area is unclassified.
NEC exhibit 515.4 gives some information which is for cryogenic material; but I am looking for flammable Class-1 Group-C material. Also figure 5.10.4 (a) of NFPA-497 does not give much information.
My question is that what happens if the height of the dike is less than 3-feet, will the classified area still end at the dike, or will it extend beyond the dike? Also in case there is no dike, then how far away from the tank will the classified area extend horizontally? What do you guys think about it? Thanks
NEC exhibit 515.4 gives some information which is for cryogenic material; but I am looking for flammable Class-1 Group-C material. Also figure 5.10.4 (a) of NFPA-497 does not give much information.
My question is that what happens if the height of the dike is less than 3-feet, will the classified area still end at the dike, or will it extend beyond the dike? Also in case there is no dike, then how far away from the tank will the classified area extend horizontally? What do you guys think about it? Thanks