It is my understanding that only fuels with a flash point under 100 degrees F would be considered hazardous. I have never had to use a classified wiring method for diesel fuel, kerosene, or heating oil. Heating oil is basically the same as diesel or kerosene. The following is from an ECM article.
Q. How does the Code address diesel fuel dispensers as they relate to hazardous locations?
A. The hazardous Class I location requirements contained in Art. 514 only apply where a flammable liquid having a flash point below 100°F [Art. 100 Volatile Flammable Liquid] is stored, handled, or dispensed [514.3(B)]. The flash point of diesel fuel is 100°F or above; thus, the area involving diesel fuel is typically not a classified location.