Hi - I have a question about a wiring method in a C1, D2 area for lighting fixtures (NEC, USA job). My scope of work does not leave the C1, D2, but will interface eventually back to an unclassified area. The start of the wiring is from a terminal junction box (NEMA 4X) , where it exits the junction box in a compression type cable gland and continues on in the cable tray to the first fixture (not factory sealed). The fixtures are HPS stanchion mount, meaning that the TC cable goes through an open conduit system and the wires terminate inside the light fixture without a cable gland or any type of sealing. The wires are connected with wire nuts, and the wiring to the next fixture goes down the same conduit and back into the cable tray. Eventually the it makes sense to continue the wiring in conduit at the ends of the runs, and the last fixtures in each run are fed with the same cable - TC, but now in an open conduit system - meaning I do not have any conduit seals when it transitions to conduit.
My question is this... I feel like when I read the code to determine whether I need cable seals or conduit seals between fixtures using this wiring method, it takes me in a loop where I can come up with two different answers. I understand that normally light fixtures would not require seals between each fixture, I'm getting hung on my wiring method.
First - 501.15(E)(1) Terminations.... Is initally talking about requiring seals where entering explosionproof boxes/enclosures. (This is not me.) , but the last sentence is "Multiconductor cables in conduit shall be sealed as described in 501.15(D)", which leads you back to C1, D1. So at every termination - every light fixture would have to be sealed. Or..... Does this last sentence only pertain to multiconductor cable in conduit entering explosionproof boxes?
Second - 501.15(E) (3) Talks about Cables Capable of Transmitting Gases or Vapors (This is me.) So this now tells me that it is not required, except for when required by 501.15(E), which is obviously listed above...
Last - My gut is telling me that the only location seals are required is on the boundary back to the unclassified area, but would like someone with more experience to confirm this. I understand that I am looking for some education. Any direction to articles, other posts, books to read on topic would be recieved well.... Thanks in advance.
My question is this... I feel like when I read the code to determine whether I need cable seals or conduit seals between fixtures using this wiring method, it takes me in a loop where I can come up with two different answers. I understand that normally light fixtures would not require seals between each fixture, I'm getting hung on my wiring method.
First - 501.15(E)(1) Terminations.... Is initally talking about requiring seals where entering explosionproof boxes/enclosures. (This is not me.) , but the last sentence is "Multiconductor cables in conduit shall be sealed as described in 501.15(D)", which leads you back to C1, D1. So at every termination - every light fixture would have to be sealed. Or..... Does this last sentence only pertain to multiconductor cable in conduit entering explosionproof boxes?
Second - 501.15(E) (3) Talks about Cables Capable of Transmitting Gases or Vapors (This is me.) So this now tells me that it is not required, except for when required by 501.15(E), which is obviously listed above...
Last - My gut is telling me that the only location seals are required is on the boundary back to the unclassified area, but would like someone with more experience to confirm this. I understand that I am looking for some education. Any direction to articles, other posts, books to read on topic would be recieved well.... Thanks in advance.