I have a situation in a C1D1 area (Headworks of a Wastewater Plant) that I need some help with.
If a conduit is routed in the concrete floor slab and turns up in a classified area and an unclassified area a conduit seal should be placed as the conduit enters/leaves the classifed location before entering/leaving the concrete floor slab. And as I understand it no additional seal is needed at the unclassified location. Correct?
Now what if a conduit is routed in the same concrete floor slab but both ends turn up the the same classified location. Should a conduit seal should be placed as the conduit enters/leaves the concrete slab?
I guess it all boils down to where the Hazardous location boundary is located. If the concrete floor slab is considered to be part of the hazarodus location then any conduit traveling through it and into new areas would make those areas classified due to the possibility of transmission of hazarous materials.
I tend to think of the concrete floor as not being part of the classified location but am having a hard time finding anything that can back me up. And if the concrete floor slab is not considered as being part of the classified location can PVC conduit be used. I see where PVC is allowed with 24" of cover and a 2" concrete envelope in a classified location (But I am assuming the floor slab is not a Classified location) but that only makes sense in areas like aircraft hangers where belowgrade is specifically noted to be C1D1. So can i use PVC conduit in the floor slab without violating code?
Thanks for any and all help. If you need any additional information let me know. NFPA 820 was used to classify the location. Code in force is 2005 NEC but would appreciate knowing what current code dictates.
If a conduit is routed in the concrete floor slab and turns up in a classified area and an unclassified area a conduit seal should be placed as the conduit enters/leaves the classifed location before entering/leaving the concrete floor slab. And as I understand it no additional seal is needed at the unclassified location. Correct?
Now what if a conduit is routed in the same concrete floor slab but both ends turn up the the same classified location. Should a conduit seal should be placed as the conduit enters/leaves the concrete slab?
I guess it all boils down to where the Hazardous location boundary is located. If the concrete floor slab is considered to be part of the hazarodus location then any conduit traveling through it and into new areas would make those areas classified due to the possibility of transmission of hazarous materials.
I tend to think of the concrete floor as not being part of the classified location but am having a hard time finding anything that can back me up. And if the concrete floor slab is not considered as being part of the classified location can PVC conduit be used. I see where PVC is allowed with 24" of cover and a 2" concrete envelope in a classified location (But I am assuming the floor slab is not a Classified location) but that only makes sense in areas like aircraft hangers where belowgrade is specifically noted to be C1D1. So can i use PVC conduit in the floor slab without violating code?
Thanks for any and all help. If you need any additional information let me know. NFPA 820 was used to classify the location. Code in force is 2005 NEC but would appreciate knowing what current code dictates.