Hazardous Locations 501.15 Sealing and Drainage

Status
Not open for further replies.

kcaf2000

Member
Location
Houston
Working a project to construct a LNG Liquefaction Facility currently in the anchor bolts down phase. My inquiry is to conduit seals in underground conduit. The method for distribution of power, control and instrumentation is from cable tray through UG Conduits to buildings and outside areas. at these locations the UG Conduits transition back into trays. Reading 501.15.B.2 exception # 2 can this be interpreted to mean that seals are not required at either end of the UG Conduit because the UG conduits turn up outside the classified area to open wiring method being cable tray?
 

Attachments

  • 01. Seals dwg 01.pdf
    113 KB · Views: 0
I think you would need a conduit seal at the div 2 end but not at the control room end. Is your sketch showing the transition to tray occurring outdoors and under the building?
 
Yes, Electrical building is installed on 7' columns with a tray system underneath out side. The othe locations to the right will be considered in Ckass 1 Div 2 area.
 