Hazardous Locations and Hospitals

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
Per the following paragragh from the NEC, do all operating rooms need to be Class I, Div 1. Are all anesthetics flammable?


517.60 Anesthetizing Location Classification.
FPN: If either of the anesthetizing locations in 517.60(A) or 517.60(B) is designated a wet procedure location, refer to 517.20.
(A) Hazardous (Classified) Location.
(1) Use Location. In a location where flammable anesthetics are employed, the entire area shall be considered to be a Class I, Division 1 location that extends upward to a level 1.52 m (5 ft) above the floor. The remaining volume up to the structural ceiling is considered to be above a hazardous (classified) location. [99: Annex E, E.1, and E.2]
 
My understanding (I'm not 100% sure, but I've been told) is that flammable anesthetics are not used in the US, and are probably only used in third world countries.

I do still see signs on some OR's that state "non-flammable anesthetics only".

Steve
 