Hello all,
I'm having a little bit of trouble determining the classification and zone of a proposed building. The client is wanting to have an accessory building built adjacent to an existing building. This building will be 10x10x10 CMU. The contents stored in this building will be fuel, propane, oxygen, and acetylene. The idea is that it will double as a small workshop later on. The building will be fully enclosed. I don't know if they intend on putting a single gas can in this space or 5.
Would you all agree that this would be considered Zone 1?
"In which ignitable concentrations of flammable gases or vapors are likely to exist under normal operating conditions; or.)
If we were to ensure there was sufficient ventilation, this enclosed space would be considered Zone 2, correct?
There must be a gas detection system in place if we wish to have any electrical in the space (receptacles, lights, welders). Gas detection needs to be tied into automatic electrical disconnect for structure, ideally located outside. Alarm will sound if concentrations reach 20% of lowest gas ignitable limit. Electrical will auto disconnect at 40%.
If there is sufficient ventilation and an alarm do light fixtures need to be explosion proof?
Thanks,
I'm having a little bit of trouble determining the classification and zone of a proposed building. The client is wanting to have an accessory building built adjacent to an existing building. This building will be 10x10x10 CMU. The contents stored in this building will be fuel, propane, oxygen, and acetylene. The idea is that it will double as a small workshop later on. The building will be fully enclosed. I don't know if they intend on putting a single gas can in this space or 5.
Would you all agree that this would be considered Zone 1?
"In which ignitable concentrations of flammable gases or vapors are likely to exist under normal operating conditions; or.)
If we were to ensure there was sufficient ventilation, this enclosed space would be considered Zone 2, correct?
There must be a gas detection system in place if we wish to have any electrical in the space (receptacles, lights, welders). Gas detection needs to be tied into automatic electrical disconnect for structure, ideally located outside. Alarm will sound if concentrations reach 20% of lowest gas ignitable limit. Electrical will auto disconnect at 40%.
If there is sufficient ventilation and an alarm do light fixtures need to be explosion proof?
Thanks,