HBL 3431 proper use.

Status
Not open for further replies.

reyamkram

Senior Member
Location
Hanover park, il
Question?

We have 240/120 3 Phase high leg delta system, we are using the HBL 3431 plug and connector , and I do not believe they are listed or approved, and they are non grounding, can they be used for grounding?
are these the proper type to be using on are system?? and if they are not, should the company replace them with the proper ones.??

any and all information we be appreciated, thank you.
 
The 4th prong is a neutral, and rated 120/208V WYE. I have never figured out what is a proper use for them.
 
What is HBL3431C

What is HBL3431C


This is what a HBL3431C is........Where in the NEC would I find, this plug is not the proper use on a 240/120 3 Phase high leg delta system?
As you can see this plug is only rated for 208/120.And it is a non grounding type plug. Thank you ,



HBL3431C
by Hubbell Wiring Device-Kellems Catalog ID: HBL3431C

Locking Devices, Twist-Lock®, Industrial, Male Insulgrip® Plug, 30A 3-Phase WYE 120/208VAC, 4-Pole 4-Wire Non-Grounding, Non- NEMA, Screw Terminal, Black and White Nylon.

  • Clear, funnel shaped wire entry for ease of termination.
  • Integral dust shield protects wiring chamber from dust or contaminants.
  • Ribbed nylon housing provides a secure grip and impact and chemical resistance.
  • Superior cord grip design protects terminations from excess strain.


 
Prpoper use for HBL3431 plug and connector body

Prpoper use for HBL3431 plug and connector body

Where in the NEC would I find, this plug is not the proper use on a 240/120 3 Phase high leg delta system?
As you can see this plug is only rated for 208/120.And it is a non grounding type plug. Thank you ,


The 4th prong is a neutral, and rated 120/208V WYE. I have never figured out what is a proper use for them.
 
We had those installed at one facility I worked. An electrician specified them, and of course, used the white terminal for ground. I changed them out to the Nema L15-30 [HBL 2811] series. Three hots and a ground, is also proper for high leg delta, as plug is rated for 250 volts 3 phase.

Do you need a 4 pole 5 wire connector for some reason? That (L21-30) is also rated for 120/208. Of course, the insulation is fine for a 240 volt high leg delta system (Specs say 2000 V!). If concerned, email Hubbell.
 