I have patient care area basic to general care in which cable type specified is HCF. I don’t see HCF in NEC 2014 anywhere or in section 517. Is it in the NEC 2014?
I suspect that the cable itself is type AC as far as the NEC is concerned.
Note that https://www.afcweb.com/ac-hcf-armored-cables/hcf-90-health-care-facilities-armored-cable/ says:
NEC250.118(8), 300.22(C), 392, 320, 517.13, 518, 645
Article 320 is for AC cable.
-Jon
Nope. You need that redundant ground.
What I mean is that what is called HFC cable is 'type AC' cable with added features to meet health care requirements.
A 'health care EMT' installation is still normal THHN in normal EMT, but with additional features required by code for health care settings. I believe that HFC cable is shorthand for AC cable with health care installation features.
Jon
HCFC has two EGC's, the metallic jacket and an insulated green conductor.
Dude, the "aluminum interlocked armor" jacket is the other ground, just like Winnie and infinity said.This HCF has no redundant EGC: https://northerncables.com/wp-content/uploads/2016/12/HCF-Solid-14_12_10.pdf
Would that satisfy 517.13?
You're correct. They are listing it as the bonding conductor in the pdf. Just another way of saying the same thing. (It has 2 grounding means)Dude, the "aluminum interlocked armor" jacket is the other ground, just like Winnie and infinity said.
Did you even look at the info in the link you posted?This HCF has no redundant EGC: https://northerncables.com/wp-content/uploads/2016/12/HCF-Solid-14_12_10.pdf
Would that satisfy 517.13?
That would be a good start !Did you even look at the info in the link you posted?
Roger
That would be a good start !
HCF = Health Care Facility and, as Roger notes, in the description on the cut sheet YOU posted it states approved for Health Care !
Yes you're correct it does not clearly state that the jacket and bonding wire combined make an EGC but it is an EGC because that is part of the construction requirement for type AC cable found in 320.100 and 320.108.Well it states it but was not sure how it would comply with 517.13 but found the answer here thanks