HCF cable

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have #8 HCF cable on plans for patient care areas fed from 40A branch circuit breaker. I have been told HCF cable comes with insulated EGC by manufacturer. What would be the min size equipment grounding conductor for HCF cable provided by the manufacturer?
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
?? Research what the manufacturer is using and if they have UL listing for the their cable. Or... if you just want to know what size EGC goes with a 40A branch circuit, look it up in the NEC.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
?? Research what the manufacturer is using and if they have UL listing for the their cable. Or... if you just want to know what size EGC goes with a 40A branch circuit, look it up in the NEC.

I know what size 40A breaker EGC would be. I am wondering with HCF cable size of #8 awg what would be the minimum ECG that comes with it typically?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Well if you already talked to the manufacturer why didn't you ask them?

Roger
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Well if you already talked to the manufacturer why didn't you ask them?

Roger

I didn’t speak with manufacturer. I don’t have cutsheet its on plans stating hcf but EGC is not shown.

HCF comes from manufacturer with insulated equipment ground. Was wondering what EGC size does it come with when phase are sized #8 awg?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I didn’t speak with manufacturer. I don’t have cutsheet its on plans stating hcf but EGC is not shown.

HCF comes from manufacturer with insulated equipment ground. Was wondering what EGC size does it come with when phase are sized #8 awg?
You said this in your first post " I have been told HCF cable comes with insulated EGC by manufacturer." so what did that mean if you had not talked to the manufacturer?

Roger
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
You said this in your first post " I have been told HCF cable comes with insulated EGC by manufacturer." so what did that mean if you had not talked to the manufacturer?

Roger

It means HCF cable comes with insulated grounding conductor by manufacturer. However the above information was not provided by the manufacturer I heard it does but not sure.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
All HCFC comes with an insulated EGC.

Contact whoever submitted the plans to you and tell them you need all the specs and submittals if that is what it will take.

Roger
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
I would rather expect 8-x HFC cable to have a ground sized like 8-x MC cable...which generally means a #10. But I agree with Roger: ask whomever submitted the plans.

If they submitted plans using 8-X HFC cable because of voltage drop on a 20 or 30A circuit, then the question might be enough to get them to recognize their error....

-Jon
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
There is this amazing tool called the Internet and if you use that and go to a cable manufacturer's web site you can view the specs on their cables OR you can come here and suffer :)

Southwire has a #8 HCF with a #8 EGC
 