I have always specified PVC Schedule 80 for outdoor underground installations. Contractor is asking to use HDPE, would this substitution be inferior, equivalent, or superior?
Thank you
You can get HDPE in Sch 80, so in that case the same. You need to make sure they are not substituting it with HDPE Sch 40.
HDPE is tougher than PVC* but not as rigid. For some applications, it's probably a better choice.
* we're allowed to shoot aerial display fireworks from HDPE tubes but not from PVC; it tends to shatter :thumbsdown:.
I have always specified PVC Schedule 80 for outdoor underground installations. Contractor is asking to use HDPE, would this substitution be inferior, equivalent, or superior?
Thank you
Have them send you a cutsheet on the particular product they intend to use and verify the wall thickness is similar to what you're proposing.
We use a lot of Duraline sch. 40 UL listed HDPE on reels. Make sure they intend to use a UL listed product, because a lot of it is not. I know that because I have to specifically mention it when ordering or else I'd get HDPE without a listing.
Also, make sure they use a UL listed transition coupling from the HDPE over to pvc/rigid/etc before it exits the ground. We use Duraline Shur-Lock II's. Again, a lot of couplings aren't UL listed. I'm sure it's because a lot of this stuff is used for utilities and they work from their own rule books.
HDPE is tougher than PVC* but not as rigid. For some applications, it's probably a better choice.
* we're allowed to shoot aerial display fireworks from HDPE tubes but not from PVC; it tends to shatter :thumbsdown:.
This is important. What do you mean by tough and rigid?
HDPE will absorb impact energy by deforming, whereas once you pass a certain strain threshold PVC will shatter. The HDPE will usually return to its pre-impact shape depending on how much oomph! is behind the impact. It's a bit like the GM Saturn vehicles with the plastic side panels. Easier to deform, but they'd bounce back from a smack with a baseball bat where a metal side panel will deform permanently.
OK so here is a summary of my investigation. I reached out to both manufacturers, the PVC - Schedule 80 that was already approved and the HDPE conduit that has been submitted. This is what I found:
PVC Schedule 80 Manufacturer: "We don't know too much about HDPE, we don't really see them as a direct competitor. We focus most of our literature on how PVC is better, lighter, quicker to install than metallic conduit."
HDPE Manufactuer: " HDPE is a superior product to PVC. A lot of people are updating their specifications and moving toward HDPE.
HDPE comes in continuous lengths. Less couplings and gluing. If you do need to couple there are special two part epoxies that need to be used to glue special HDPE couplings. There are also HDPE Shurlock couplings which are UL listed and can transition to just about any other conduit system. HDPE when laid in a trench is flexible enough to get around most obstacles. The one thing that is worse about HDPE is that it does have more of an expansion contraction issue than PVC. Though it being underground that should not be as much of an issue. HDPE can be installed at -40Def F while PVC gets very brittle at a little below freezing. Wall thickness is similar between PVC and HDPE and you can see how they compare, you can get a Schedule 80 HDPE conduit and that will actually be slightly thicker than the PVC schedule 80 conduit. Not all HDPE is UL listed though, only Schedule 40, Schedule 80, and SDR 13.5 HDPE can be UL listed. If you don't ask for it you will not get the UL listed one."
Since HDPE can only be installed underground, I don't see it having a worse contracts expansion properties much of an issue. It seems like there are some serious cost benefits to using HDPE duct and as it starts to get more accepted it will surpass PVC at least for all underground installations.
Especially with the built-in pull tape!I'm guessing that by the time you have bent over a trench gluing together 20 foot sticks of PVC for a 1000 foot run, you're real ready to look at HDPE.
Especially with the built-in pull tape!
NEC says you cannot pull the wires before the conduit run is complete, but does not care about the pull tape.
Really? Duraline will sell you the conduit with the conductors already in it.
You're taking what Golddigger is saying out of context.
Cable-in-conduit is a premanufactured assembly from the factory, you know that, and it doesn't make what Golddigger said any less true.
The hdpe stuff has me looking... only have another two floors to build but, it looks like a lot less work to use. Still watching prices for my next trip to Jamaica. I hope to hear how others are faring with it in concrete... YouTube promos show it to be pretty good but they show a lot of things that don’t work..lol
like steel door frames