Questions are in regard to health care facilities, operating rooms (anesthetizing locations) and medical equipment. Can medical equipment cords be extended up to 18 feet?
1) Questions are being posed as to extention cords allowed in anesthizing locations?
2) NFPA 99 (2002 edition) 8.4.1.2.4 (1 % 5) referr to cords shall be continuous with no limit in length. I have heard that a portable electrical appliance (Medical Device?) cord can be up to 18 feet max. However, the NEC states only 6ft allowed and that is how equipment is shipped.
3) Line isulation panels. From my understanding they are only required in wet operationg rooms up to 300 micro amps max.
1) Questions are being posed as to extention cords allowed in anesthizing locations?
2) NFPA 99 (2002 edition) 8.4.1.2.4 (1 % 5) referr to cords shall be continuous with no limit in length. I have heard that a portable electrical appliance (Medical Device?) cord can be up to 18 feet max. However, the NEC states only 6ft allowed and that is how equipment is shipped.
3) Line isulation panels. From my understanding they are only required in wet operationg rooms up to 300 micro amps max.