What space? Patient care space? Office space? Electric room space? Help us help you. Be more specific.Originally posted by sleepy:
under slab is under the space
517.10 Applicability
(A) Applicability Part II shall apply to patient care areas of all health care facilities.
(B) Not Covered Part II shall not apply to the following:
(1) Business offices, corridors, waiting rooms, and the like in clinics, medical and dental offices, and outpatient facilities
(2) Areas of nursing homes and limited care facilities wired in accordance with Chapters 1 through 4 of this Code where these areas are used exclusively as patient sleeping rooms
Roger517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas
Wiring in patient care areas shall comply with 517.13(A) and 517.13(B).
(A) Wiring Methods All branch circuits serving patient care areas shall be provided with a ground path for fault current by installation in a metal raceway system, or a cable having a metallic armor or sheath assembly. The metal raceway system, or metallic cable armor, or sheath assembly shall itself qualify as an equipment grounding return path in accordance with 250.118.
A metal raceway must be used to serve this area regardless of whether it is in the ceiling, walls, or under the slab.517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas
Wiring in patient care areas shall comply with 517.13(A) and 517.13(B).
(A) Wiring Methods All branch circuits serving patient care areas shall be provided with a ground path for fault current by installation in a metal raceway system. The metal raceway system shall itself qualify as an equipment grounding return path in accordance with 250.118.
So is this conduit feeding something in the patient care area or is simply within the concrete and terminating somewhere else?ok i see in 517.13 about cable having metallic armor or sheathing. we have a dental area on the first floor where the contractor has run pvc in the concrete slab under our space. is there anywhere that the code mentions about concrete slab. thank you
IF the PVC is "just passing through" so what! The point is--does the PVC conduit feed any branch circuit in the patient care space? Now if the PVC is feeding the floor outlet under the dental chair, YOU have a violation!Originally posted by sleepy:
we have a dental area on the first floor where the contractor has run pvc in the concrete slab under our space.
Originally posted by roger:
Sleepy, I agree with you that this space must use metal raceways underslab.
517.10 Applicability
(A) Applicability Part II shall apply to patient care areas of all health care facilities.
(B) Not Covered Part II shall not apply to the following:
(1) Business offices, corridors, waiting rooms, and the like in clinics, medical and dental offices, and outpatient facilities
(2) Areas of nursing homes and limited care facilities wired in accordance with Chapters 1 through 4 of this Code where these areas are used exclusively as patient sleeping roomsRoger517.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas
Wiring in patient care areas shall comply with 517.13(A) and 517.13(B).
(A) Wiring Methods All branch circuits serving patient care areas shall be provided with a ground path for fault current by installation in a metal raceway system, or a cable having a metallic armor or sheath assembly. The metal raceway system, or metallic cable armor, or sheath assembly shall itself qualify as an equipment grounding return path in accordance with 250.118.