Mike Burch
Member
- Location
- Apache Junction, Arizona
We have two panel boards up on the roof of the hospital right next to each other. One is fed with emergency power (600A) from a transfer switch and the other is on the normal power source (1000A) and very lightly loaded. For some reason the patient room air handlers were not put on e power. The loads on the e power panel are elevators and exhaust fans and I think they would be considered critical power. My question is would it be in violation of 517.30 Part C1 to have the normal source circuits occupy space in the same cabinet with the critical circuits? As in pick up the air handlers but feed them from the critical load panel through a wireway between the two cabinets. In the book it mentions the life safety branch and critical branch shall not enter the same raceway, box or cabinet but would this be similar violation? This might be an easy work around but it may turn out to be major surgery. :grin: Thank you in advance. Mike
