electricalist

Senior Member
Location
dallas tx
In my patient care rooms Im to install tape light under the cabinets.
Im going to use the same circuit that feeds the counter top gfci that is on a ats.
If I get a hardwire driver and put it above the cab or ceiling can I run my low voltage free in the wall and come out in the bottom of the cab like it was for a florescent.?

Sent from my GT-N5110 using Tapatalk
 
According to 517.80 (2011 NEC), low voltage systems in patient care areas need to be treated similar to branch circuits.

So a free air installation of cable or wire in the wall would not be allowed. But you might be able to fish hospital grade MC cable through the wall.
 