B billnye New member Location chambersburg,pa Dec 23, 2014 #1 Does a switch in a patient exam room require HealthCareMC feeding overhead lights, exhaust fan and undercounter lights?
Does a switch in a patient exam room require HealthCareMC feeding overhead lights, exhaust fan and undercounter lights?
roger Moderator Staff member Location Fl Occupation Retired Electrician Dec 23, 2014 #2 Read 517.13 (A) and (B) taking note of Exception2 and if the circuit is on the Critical branch read 517.30(C)(3)(3), you may need to use a non-flexible metallic wiring method. Roger
Read 517.13 (A) and (B) taking note of Exception2 and if the circuit is on the Critical branch read 517.30(C)(3)(3), you may need to use a non-flexible metallic wiring method. Roger