heat element

Status
Not open for further replies.

mannyb

Senior Member
Location
Florida
Occupation
Electrician
Today had a service call at restaurant and heat strip at plate warmer station
trippping breaker, checked temp buttom ok removed strip from circuit it stop tripping
reconnected it started tripping breaker again. I checked ohms on heat element seemed
ok. I connected heat strip direct to breaker it stayed on. Reconnected to strip it stopped
working. Any ideas?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
when you connected the strip directly to the breaker was it mounted the same as always ?
 

jeremysterling

Senior Member
Location
Austin, TX
I worked on one of these the other day. Tripping the breaker. It was on a BR230. Nameplate amps at 23.9A. The ampclamp says 23.7A @ 211V. Must be the 80% breaker.

I replaced the "infinite switch" thermostat and the breaker. The breaker was about three years old. This fix will probably work for a year or two. As soon as lunch starts they crank the switch to max where it stays the rest of the day.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is it possible that when the heating element is mounted you have leakage current to the surface on which it is mounted.
(might need a megger to check)
 

mannyb

Senior Member
Location
Florida
Occupation
Electrician
Is it possible that when the heating element is mounted you have leakage current to the surface on which it is mounted.
(might need a megger to check)

I took heat element to repair shop the guys there said it maybe under stress when installed
weaking layers inside element. I hope when I go install new ones tomorrow it doesnt trip
or i'll look pretty stupid.
 