Calculatiing heat load for an electrical building, to give my HVAC counterpart for the design on air conditioning.
Reffering to standard practices, i notice the heat loss on demand load of the equipments are factored as directly proportional to the full load heat loss.
Where the heat loss is Square of (I) * R, so for a 50% demand, which is I/2 , the heat loss is a quarter(or 25%) of the full load heat loss, not 50% of full load heat loss.
i am trying to find technical standards. papers on this subject but whatever i read considering a direct proportional reduction on heat.
have anyone have experiance on this, where the "Square of (I) * R" function applied to arrive the heat load for the demand load. Highly apprecaite if one can share their experiance or thought.