JJWalecka
Senior Member
- Location
- New England
The 26 would allow you to round up to a 30A fuse since 26 is not a standard size.I wonder why they specify a different size fuse than the breaker? I've never seen a nameplate list it like that.
Where is it stated that you can round up OCPDs to the next standard size?The 26 would allow you to round up to a 30A fuse since 26 is not a standard size.
Perhaps its a mistake, or perhaps the trip curve of a 30A fuse is similar to a 25A breaker.
240.4(B)Where is it stated that you can round up OCPDs to the next standard size?
If you installed a 30 amp breaker for a unit that has 15 max requirement, the inspector should fail you. I would.inspector shot down my equipment protection. i ran 10ga on a double 30, and the equipment was only rated for 15. Fail. had to pull the 30amp and install the 15.
It states maximum size so you cannot round up. You either find a 26 amp fuse or round down to 25 amps.The 26 would allow you to round up to a 30A fuse since 26 is not a standard size.
Perhaps its a mistake, or perhaps the trip curve of a 30A fuse is similar to a 25A breaker.
Don do you have a code reference for that? I am looking at 440.22(A) Exception 1. [2023 NEC]It states maximum size so you cannot round up. You either find a 26 amp fuse or round down to 25 amps.
I would think 110.3(B). Neither 240.4(B) nor 440.22 give you license to ignore the manufacturer's max fuse or circuit breaker marking. (Especially not 240.4, which is titled 'Protection of Conductors' and does not apply to equipment.)+Don do you have a code reference for that? I am looking at 440.22(A) Exception 1. [2023 NEC]
It states maximum size so you cannot round up. You either find a 26 amp fuse or round down to 25 amps.
Then what is 440.22(A) exception #1 for? What is that exception for if not rounding up to the next standard size?nor 440.22 give you license to ignore the manufacturer's max fuse or circuit breaker marking.
Motors that don't come with a max fuse marking?Then what is 440.22(A) exception #1 for?
440.22(A) does not apply directly to the equipment shown in the OP. It applies only to an individual motor compressor without any other loads present. The equipment in the OP also includes a fan, so it falls under 440.22(B).Then what is 440.22(A) exception #1 for? What is that exception for if not rounding up to the next standard size?
Okay I see the rounding up does not apply to the OP's unit. It would apply to an individual motor compressor without any other loads present and possibly only if your under the 2023 NEC. I am not sure if that exception is new to the 2023 or they re-worded it, I suspect its new.440.22(A) does not apply directly to the equipment shown in the OP. It applies only to an individual motor compressor without any other loads present. The equipment in the OP also includes a fan, so it falls under 440.22(B).
Now when the motor compressor is the largest load (typical case), 440.22(B)(1) applies and it refers to the "value specified in 440.22(A)" plus the sum of the other loads. Presumably the maximum fuse size is the result of the manufacturer doing that 440.22(B) calculation. Which calculation may already include the use of the 440.22(A) exceptions.