I am both and electrical engineer and contractor. We were recently installing a generator in a large building and disconnected power to one of the server rooms (as part of a scheduled shutdown). My crew disconnected all the panels feeding this room and shut off the fan coil unit (FCU) serving this area. However, the exterior heat pump (which was paired with this FCU is located several floors below) was not turned off. Total power outage was approximately 6 hrs. The compressor in the heat pump failed as a result of this shutdown (to the interior FCU). The units were about 2-3 years old and the manufacturer agreed to replace the compressor itself under warranty, but the building wants us to cover the ~$10k of labor and misc. materials required to install it, flush the lines, etc.
We've installed hundreds of HVAC systems (and I've designed the electrical supply to several myself). I've never seen an electrical interlock between exterior and interior split system components (except in the larger or BMS controlled units) - not including those like the Mitsu's where one unit feeds the other. In this case, there are only thermostat wires run along with the lineset. My question is, should I be designing some type of interlock system so that the exterior unit will shut down in the event that the FCU fails? There are many reasons this could happen including a seized fan, belt tear, breaker failure, shunt trip, someone simply shutting down the unit, etc.
I had always assumed that the pressure switches integral to all modern heat pumps/AC units would shut down the system in the event that airflow was compromised in the FCU (probably the low pressure would trip first as the evaporator starts to ice up). Also, most modern compressors have heat sensors and other protective devices. With this particular manufacturer, the thermostat transformer is located in the exterior unit, but the wiring goes through the FCU before the thermostat, so it would be very easy to install a relay which would shut down the thermostat in the event the FCU lost power.
Any comments or siggestions? Thanks in advance.
I am both and electrical engineer and contractor. We were recently installing a generator in a large building and disconnected power to one of the server rooms (as part of a scheduled shutdown). My crew disconnected all the panels feeding this room and shut off the fan coil unit (FCU) serving this area. However, the exterior heat pump (which was paired with this FCU is located several floors below) was not turned off. Total power outage was approximately 6 hrs. The compressor in the heat pump failed as a result of this shutdown (to the interior FCU). The units were about 2-3 years old and the manufacturer agreed to replace the compressor itself under warranty, but the building wants us to cover the ~$10k of labor and misc. materials required to install it, flush the lines, etc.
We've installed hundreds of HVAC systems (and I've designed the electrical supply to several myself). I've never seen an electrical interlock between exterior and interior split system components (except in the larger or BMS controlled units) - not including those like the Mitsu's where one unit feeds the other. In this case, there are only thermostat wires run along with the lineset. My question is, should I be designing some type of interlock system so that the exterior unit will shut down in the event that the FCU fails? There are many reasons this could happen including a seized fan, belt tear, breaker failure, shunt trip, someone simply shutting down the unit, etc.
I had always assumed that the pressure switches integral to all modern heat pumps/AC units would shut down the system in the event that airflow was compromised in the FCU (probably the low pressure would trip first as the evaporator starts to ice up). Also, most modern compressors have heat sensors and other protective devices. With this particular manufacturer, the thermostat transformer is located in the exterior unit, but the wiring goes through the FCU before the thermostat, so it would be very easy to install a relay which would shut down the thermostat in the event the FCU lost power.
Any comments or siggestions? Thanks in advance.