Rewire

Senior Member
I have two heat pumps each needing a 100A ,I want two set a single 200A panel and feed both from it I cannot find anythig that prohibits this any input would help.
 
As long as you provide proper overcurrent protection (ground-fault and short circuit protection), and properly size branch circuits to each unit from the 200-ampere panelboard, you should be good to go.
 
pgordon said:
what about 210.19 , 215.2. cotinuous loads ???

If we assume the 100 amps is already figured in with the 100 amp breaker and feeder than you would not need to do it again. Also I would not consider a heat pump continuous load but it doesn't matter since we need to figure it at 125% anyway.
 