J jrfbuildit Member Location Chester County, Penna. Jan 27, 2011 #1 Will a GFCI receptacle feeding heat tape that has "built in" GFCI protection have the possibility of canceling each other out?
Will a GFCI receptacle feeding heat tape that has "built in" GFCI protection have the possibility of canceling each other out?
raider1 Senior Member Staff member Location Logan, Utah Jan 27, 2011 #3 It wouldn't cancel each other out and would not cause any problem other than not knowing which GFCI device would trip first in a ground fault condition. Chris
It wouldn't cancel each other out and would not cause any problem other than not knowing which GFCI device would trip first in a ground fault condition. Chris
bluesmoke...oops Senior Member Location Tri-Cities, Washington Jan 27, 2011 #4 Does the heat tape gfi or gfe built into it?