1. Is NEC Article 427 only article apply to electric heater type MI cable for pipe heating? For example, MI article 332 does not apply.
2. NEC 427.23 (2011) requires electric heating equipment shall be listed and have a grounded conductive covering for an effective ground path. This implies the heater cable shall be listed to have the seamless metallic alloy (corrosive resistant with high nickel content) covering provide return path for the OCD. We are waiting for the MFG to prove their product is properly listed to perform as an EGC.
a. How can we verify with the MFG future submitted documents that their product is properly listed and tested?
b. Can it be any lab Canada versus UL?
Thank you for the advise, limited experience in specialty material and this is critical.
2. NEC 427.23 (2011) requires electric heating equipment shall be listed and have a grounded conductive covering for an effective ground path. This implies the heater cable shall be listed to have the seamless metallic alloy (corrosive resistant with high nickel content) covering provide return path for the OCD. We are waiting for the MFG to prove their product is properly listed to perform as an EGC.