- Location
- Windsor, CO NEC: 2017
- Occupation
- Hospital Master Electrician
How often would you say you've seen heat trace fail at the end of its life showing overcurrent versus undercurrent (or an open)?
A friend and I are mulling over possible solutions for an embedded heat trace cable that is kicking the breaker. The hope is that all is not lost and that the cable can be salvaged, and that there is some aspect of the problem that we are not seeing.
This is 277v heat trace that at some point in the past few years has been set to activate whenever the moisture sensor is triggered, regardless of outside temperature. To add insult to injury, GFPE was not functional during this period. My thought is that even though generally heat trace is self-regulating despite the settings at the controller, being energized during any summer rain has broken down the insulation of the tape and it is not salvageable.
The run does not megger, it's resistance to the circuit EGC is in the 100 ohm range.
As a follow-up question, I have been forced to ask myself what GFPE is supposed to accomplish in this scenario (since the knee-jerk reaction is to point a finger at the lack thereof). Suppose it were enabled when problems first arose, is the thought that it would deenergize the cable when things were just slightly askew in the hope that a single point could be repaired, or is it simply for protection against possible ignition due to failing cable grounding itself out as it went bad?
A friend and I are mulling over possible solutions for an embedded heat trace cable that is kicking the breaker. The hope is that all is not lost and that the cable can be salvaged, and that there is some aspect of the problem that we are not seeing.
This is 277v heat trace that at some point in the past few years has been set to activate whenever the moisture sensor is triggered, regardless of outside temperature. To add insult to injury, GFPE was not functional during this period. My thought is that even though generally heat trace is self-regulating despite the settings at the controller, being energized during any summer rain has broken down the insulation of the tape and it is not salvageable.
The run does not megger, it's resistance to the circuit EGC is in the 100 ohm range.
As a follow-up question, I have been forced to ask myself what GFPE is supposed to accomplish in this scenario (since the knee-jerk reaction is to point a finger at the lack thereof). Suppose it were enabled when problems first arose, is the thought that it would deenergize the cable when things were just slightly askew in the hope that a single point could be repaired, or is it simply for protection against possible ignition due to failing cable grounding itself out as it went bad?