chuckgassmannm
Member
- Location
- el paso tx el paso
I'm trouble shooting some heat trace. The branch circuits are 277 v single pole gfci 30 amp breakers. One of the circuits keeps tripping., even with out a load. After disconnecting the wires at the panel and from the heat trace cable. When I check the voltage between the neutral and ground I get a reading of 60 v ac. There are two other circuits running in parallel. When I turn off 1 of the circuits the voltage drops to 30 v and when I turn off the other one it drops to.v 6 volts. Can that be induced voltage? I'm suspecting a bad breaker. But the voltage reading is getting me side tracked. Thanks