D Dexie123 Senior Member Dec 29, 2013 #1 What is the typical protocol when putting OCPD for heat trace wiring? I would think this is "deicing" equipment and would not require GFI protection.
What is the typical protocol when putting OCPD for heat trace wiring? I would think this is "deicing" equipment and would not require GFI protection.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Dec 29, 2013 #2 See 426.28 GF protection IS required for most heat trace wiring. It is, however, GF protection in the 30 ma range and not GFCI 5 ma protection
See 426.28 GF protection IS required for most heat trace wiring. It is, however, GF protection in the 30 ma range and not GFCI 5 ma protection
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Dec 29, 2013 #3 Is this an Article 427 installation or Article 426? Heat tracing and deicing are somewhat different.