phineascage
Member
- Location
- Gaffney, SC
Forgive me if this has been covered before. I have so far not found the answer to my question. I am struggling with a GFCI type breakers feeding heat trace circuits that immediately trip when energized. These are Square D Series 2 Type QO breakers. The heat tracing is Raychem 5BTV2-CT self regulating heating cable. I have tested and retested the heat tracing as the manufacturer suggests, megging the circuit at various voltages up to 2500V and measuring continuity between the heat trace conductors. The insulation resistance test provided 1T ohm and the continuity between the conductors was around 30ohms for a roughly 20' run of the heat trace. These values are well within design specifications of the heat tracing. I am now talking to online tech support with Schneider/Square D and the best I can get from the person I'm talking to is that the grounding and neutral must be segragated in the sub panel. Our system consists of a delta-wye transformer 480/208VAC transformer feeding an outdoor heat trace panel. Initially the neutral was bonded to ground in this heat trace panel. I removed this ground connection and still received the same results, breaker immediately tripping when energized. I contacted Scheider again and this time was told the same thing but also that continuity between the neutral and the panel ground must be greater than 1M ohm. In our system I measure roughly 7 ohms from neutral to panel ground which can only mean that the neutral bonding to ground is happening upstream from the heat trace panel. I have asked for documentation spelling out grounding and neutral requirements for these breakers but the response I received was that this is an NEC question. I then asked for documentation spelling out the greater than 1M ohm continuity requirement between neutral and ground for these breakers and the response I received with this was that this is an industry standard and not spelled out at least in their documentation. Have any of you guys run into this sort of issue before? I know the heat trace circuit and breaker are fine. I have operated the heat tracing from a 120VAC GFCI receptacle with no problems. I have swapped the circuit feed from one Square D breaker to a spare unused one in the panel and received the same immediate trip. I can disconnect the circuit at the breaker and it will not trip. The test button on the breaker also trips the breaker. I am by no means a good electrician so I was hoping to get some help here. I appreciate anyone reading through this long winded description. If anyone has any questions, please ask. Thank you.