my 13200 / 7620 KV Y transformer emits abnormal heat even it is underloaded at 30% loading can anybody help me? if i cannot solve this i might be terminated!!!:D
 

nakulak

Senior Member
some information would be helpful.

trans model #, check pri amps on all phases, an idea of the temp, maybe a pic ?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
More questions.
Where is the excess heat, the radiators, the bushings, or the tanks? How are you measuring the heat, just looking at the temperature guage?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
"abnormal" definitely needs to be quantified.
I've seen a few cases of "abnormal" heat with properly loaded transformers that can be attributed to their not being level and having an oil flow problem.
In one case there was blockage in the oil path to some of the "fins"
 

zog

Senior Member
Location
Charlotte, NC
"abnormal" definitely needs to be quantified.
I've seen a few cases of "abnormal" heat with properly loaded transformers that can be attributed to their not being level and having an oil flow problem.
In one case there was blockage in the oil path to some of the "fins"

Thats what I am guessing too, common problem to have restricted flow in the fins, should look like this.
 

barclayd

Senior Member
Location
Colorado
Thats what I am guessing too, common problem to have restricted flow in the fins, should look like this.

Does the image really show restricted flow?
85 Deg F doesn't seem very hot - I'm hotter than that.
The circulation depends on a temperature difference between the top and bottom.
Just because a surface is too hot to touch doesn't necessarily mean the device is overheated.
db
 

zog

Senior Member
Location
Charlotte, NC
Does the image really show restricted flow?

No, I said it should look like that

85 Deg F doesn't seem very hot - I'm hotter than that.

this was outside in winter in Michigan, ambeient was around freezing.

The circulation depends on a temperature difference between the top and bottom.Just because a surface is too hot to touch doesn't necessarily mean the device is overheated.
db

Right
 

480sparky

Senior Member
Location
Iowegia
I had similar concerns on a transformer install I did... it was just too hot to touch. I read 286?F is some places. Contacted the manufacturer, and they said that's normal.:cool:
 

Fulthrotl

~Autocorrect is My Worst Enema.~
Help me out here. What is a "bowsered"?

cf

bowsering is the process of pulling a vacuum on an oil filled xfmr,
and circulating the oil thru a "bowser", which is a water separator,
filter media, and heating assembly.

the purpose is to lower the dew point of any moisture remaining
in the oil, by increasing temperature, and lowering pressure, to
cause the water to boil off.

at the same time, the oil is filtered of particulate matter. it is sometimes
called "polishing" the oil.

the process continues until oil samples being tested, come back
clean and dry enough to satisfy the powers that be. i've gotten stuck
on a difficult one that ran a week and a half.... energy pumped into the
oil as heat normally require 200a. of 480vac. the one i did had the xfmr
at 178 degrees for a week, and that was 35,000 gallons of oil.

it's a pain in the butt. 12 on, 12 off, for 12 days, and i had 6pm to 6am.
 

Besoeker

Senior Member
Location
UK
I had similar concerns on a transformer install I did... it was just too hot to touch. I read 286?F is some places. Contacted the manufacturer, and they said that's normal.:cool:
I agree. The manufacturer should be able to provide a test sheet with losses and designed winding and oil temperature rises.
I think that should be the starting point.
 

zog

Senior Member
Location
Charlotte, NC
I agree. The manufacturer should be able to provide a test sheet with losses and designed winding and oil temperature rises.
I think that should be the starting point.

The max rise limits are on the nameplate, if they are exceeded life expentancy decreases dramaticly.
 

480sparky

Senior Member
Location
Iowegia
I agree. The manufacturer should be able to provide a test sheet with losses and designed winding and oil temperature rises.
I think that should be the starting point.

Not sure what ever happened, as I sent my test results to the factory.

The clowns in the office (I was working for wages then) took it from there. AFAIK, nothing ever happaned to it.
 