kbsparky
Senior Member
- Location
- Delmarva, USA
I have a customer with a bathroom with the warm tiles heating system installed in one of his bathrooms.
After about a year in operation, the built-in GFCI on the thermostat began tripping. Initially, resetting the unit would work for awhile, but later it would not set at all. The system operates at 120 Volts, but the thermostat is capable of using either 120 or 240 Volts.
Without busting up the floor and installing a new system, how would one troubleshoot and repair such an installation?
We decided to install an isolation transformer downstream of the thermostat, change the circuit and thermostat to 240 Volt input, and wired the transformer for 240 input, 120 output.
This scenario has worked fine since the installation of the transformer. No more nuisance tripping.
Have any of you utilized this solution for this type of problem?
After about a year in operation, the built-in GFCI on the thermostat began tripping. Initially, resetting the unit would work for awhile, but later it would not set at all. The system operates at 120 Volts, but the thermostat is capable of using either 120 or 240 Volts.
Without busting up the floor and installing a new system, how would one troubleshoot and repair such an installation?
We decided to install an isolation transformer downstream of the thermostat, change the circuit and thermostat to 240 Volt input, and wired the transformer for 240 input, 120 output.
This scenario has worked fine since the installation of the transformer. No more nuisance tripping.
Have any of you utilized this solution for this type of problem?