We are installing 5kW heaters in some storage trailers and I had a couple of questions regarding the branch circuit installation. Each heater circuit (3) total will be fed from a 120/240V panel. Heaters are rated 208-240V.
At 240V a 5kW heater draws 20.8A. Do we need to take 125% of this value since heater will run continuously. If so this gives us 26A. Does this mean that we need to use a #10AWG (ignoring voltage drop). If so we would use a 30A OCPD?
Can we round the heater load calc down to 20A muliply this by 125% to come up with 25A and then use a #12AWG? If so I dont think a #12 is permitted to be on an OCPD greater than 20A so this then forces us to use #10?
Do we need some sort of disconnect in the storage trailer (conex) or can we wire the branch circuit straight into the heater.
Circuit will be underground in PVC for small 10-20ft length. Do we need to derate for this underground routing? What factor would be applicable?
At 240V a 5kW heater draws 20.8A. Do we need to take 125% of this value since heater will run continuously. If so this gives us 26A. Does this mean that we need to use a #10AWG (ignoring voltage drop). If so we would use a 30A OCPD?
Can we round the heater load calc down to 20A muliply this by 125% to come up with 25A and then use a #12AWG? If so I dont think a #12 is permitted to be on an OCPD greater than 20A so this then forces us to use #10?
Do we need some sort of disconnect in the storage trailer (conex) or can we wire the branch circuit straight into the heater.
Circuit will be underground in PVC for small 10-20ft length. Do we need to derate for this underground routing? What factor would be applicable?