Gentlemen,
I am hooking up three single phase 480VAC 5000W resistive heaters in a delta configuration to a three phase contactor and breaker in an industrial control panel fed by 480VAC. Am I correct in calculating the three phase load at 18.1 amps? One of my electricians thought that it might be different result for resistive and inductive loads connected this way. Thanks
I am hooking up three single phase 480VAC 5000W resistive heaters in a delta configuration to a three phase contactor and breaker in an industrial control panel fed by 480VAC. Am I correct in calculating the three phase load at 18.1 amps? One of my electricians thought that it might be different result for resistive and inductive loads connected this way. Thanks