Divide 208 by 240 times 4000 and you get 3466 Watts.
The old saw about lower voltage means more amps does not work for resistive loads.
Divide 208*208 by 240*240 and multiply that by 4000 and you will get the right answer: 3004 watts.
208/240 alone just gives you the decrease in the current.
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
A 4,000watt heater connected 240 volt consumes how many watts connected 208 3 phase? I get 4,800watts. Is this correct?
Not sure what is happening here. Is this a 3 phase heater or a single phase heater?
If you use single phase and go from 240v to 208v then you will have about 75% less wattage at the 208V. 75% of 4000~= 3000 watts...
kwired
Electron manager
NE Nebraska
Where I learned math, take 75% away from 4000 and it leaves you with 1000 take 25% away from 4000 and it leaves you with 3000.
But sometimes they change things without telling me;)
Dennis Alwon
Chapel Hill, NC
You are correct -- it is 75% of the 240V wattage not what I stated but I did do the math correctly - at least :p